I'll give them a call tmrw, I've be asked by the company setting it up for a 200a 3ph supply... It's a 2nd hand machine, they are doing the air lines and setting up machine, I'm doing the power but there is only 200a 3ph for the whole site.... Just wanted some details on full load @ 100% running before pulling the plug... Seems way to big.

Cheers
 
from what i can see, it's 75kW. thats about 105A/phase.
 
200A supply? It just isn’t going to do it. With a soft start maybe, but there’s the rest of the loading to take in to account.
 