Hey guys

Situation:
I’m replacing a double socket on a ring circuit that also has a spur feeding an FCU (for a TV). The existing conductors aren’t long enough to connect directly to the new MK Pro socket.

Setup:
I’m using an MK surface box for the installation. Cable size 2.5mm Twin and E

Plan:
To manage the short conductors, I’m going to extend them with 3-port Wago connectors inside the surface box. For each conductor type (Live, Neutral, Earth):

  • The ring incoming leg and the spur conductor will share one Wago.
  • The ring outgoing leg will have its own separate Wago.
  • From each Wago, a short tail will run to the corresponding terminal on the MK Pro double socket.

This means each socket terminal will have two tails: one from the Wago joining ring in + spur, and one from the Wago for ring out. The spur is tapped off inside the same Wago as the ring in leg.

Questions:

  • Is this setup safe and compliant?
  • Will it maintain ring continuity without breaking the ring?
  • Is it suitable for a spur drawing close to 13A continuously?
  • Any concerns about earth continuity or bonding, considering the MK surface box is PVC?
 
Is this setup safe and compliant?
Yes
Will it maintain ring continuity without breaking the ring?
A standard continuity test will confirm if it has or hasn't.
Is it suitable for a spur drawing close to 13A continuously?
What is the rating (A) of the Wago connector? If greater than 13A - Yes

Any concerns about earth continuity or bonding, considering the MK surface box is PVC?
No, the earth continuity is made via the socket terminals and again, a standard continuity test will confirm compliance.
 
Yes

A standard continuity test will confirm if it has or hasn't.

What is the rating (A) of the Wago connector? If greater than 13A - Yes


No, the earth continuity is made via the socket terminals and again, a standard continuity test will confirm compliance.

Thank you so much . Figure of 8 at consumer unit? And just checking at the socket ?
 