i would just run cable to greenhouse and long as rcd protected and suitable enclosure for conditions , think ipx4 should be fine , if any two parts are at arms reach from eachother you could suplementry bond..
 
Pat Tester,

What i'm saying is that with a TT system, the more rod's you drive into the ground the better the Final Ra is going to be. If you connect the rods for the garage shed and greenhouse via a 3rd core of a SWA cable to the EMT at the garage CU the 3rd core of the supply SWA cable will take those Rod installations back to the MET. Use the SWA armouring as your CPC for the supply and distribution cables.

Personally, the shed and the greenhouse can both be supplied from the Garage CU on one or two radial circuits. As stated earlier nothing to stop you supplementary bonding the greenhouse metalwork to one of the sockets....
Depth n all eng........
 
i would just run cable to greenhouse and long as rcd protected and suitable enclosure for conditions , think ipx4 should be fine , if any two parts are at arms reach from eachother you could suplementry bond..
IP4X in a greenhouse?, think about it! Watering plants, auto watering system etc.
 