H, I know this has probably been covered a thousand times, but just interested to here what people wouldn't of on this set up feeding a brick garage with steel frame And sprinkler system that will need bonding


TN-C-S (200amp) 70mm tri-rated tails (50mm Earth)(25mm bonds)➡️DB1➡️ Out off DB1 with 16mm 3core via 45amp mcb to garage DB

now should this garage be put on its own TTsystem with the earth wire isolated?

or should I drag 25mm bonds from the steel and water to the main building MET

if anyone can point me to a reg or info on this it would be much appreciate
 
H, I know this has probably been covered a thousand times, but just interested to here what people wouldn't of on this set up feeding a brick garage with steel frame And sprinkler system that will need bonding


TN-C-S (200amp) 70mm tri-rated tails (50mm Earth)(25mm bonds)➡️DB1➡️ Out off DB1 with 16mm 3core via 45amp mcb to garage DB

now should this garage be put on its own TTsystem with the earth wire isolated?

or should I drag 25mm bonds from the steel and water to the main building MET

if anyone can point me to a reg or info on this it would be much appreciate

What type of cable is the 16mm 3 core?
 
Keeping the TN-C-S earth and bonding the extraneous conductive parts back to the MET would be my preferred choice. If it isn't feasible to do so then making the the outbuilding installation a TT system , isolating the TN-C-S earth at outbuilding and bonding the extraneous conductive parts at the outbuilding back to the sub board will be fine.
 
If this is a new install then just run 25mm² 3 core SWA out there, bond the metalwork in the garage back to the garage DB as an EMT and use the 25mm² core as combined earthing and bonding conductor back to DB1.
Depending on distance and so cost, you might be able to run it as 4 core 16mm² SWA and use two cores as the combined conductor in parallel.


As far as practicable you want to maintain the best earthing arrangement you can.
Guidance note 8 provides some useful information regarding maintaining earthing and bonding on multiple buildings.
 
H, I know this has probably been covered a thousand times, but just interested to here what people wouldn't of on this set up feeding a brick garage with steel frame And sprinkler system that will need bonding


TN-C-S (200amp) 70mm tri-rated tails (50mm Earth)(25mm bonds)➡️DB1➡️ Out off DB1 with 16mm 3core via 45amp mcb to garage DB

now should this garage be put on its own TTsystem with the earth wire isolated?

or should I drag 25mm bonds from the steel and water to the main building MET

if anyone can point me to a reg or info on this it would be much appreciate
Why the hell would anyone want to ditch a perfectly good TNCS system for a slapdash TT lashup is beyond me!!! lol!!!
Your not exporting anything!!! lol!!! It's called extending!!!!lol!!
(you can thank me later Eng!)
 
Why the hell would anyone want to ditch a perfectly good TNCS system for a slapdash TT lashup is beyond me!!! lol!!!

Well for one it may be a lot easier & less expensive. Especially if the armoured is already in place.
Also it's not a lash up, it's just another method, perfectly acceptable.
 
From what i can make out from the OP of this thread, this doesn't sound like your typical domestic garage install but rather a commercial or industrial set up especially as it has it's own sprinkler system. Though we as usual get very little information to base anything on.....

So far from being over the top, it makes far better sense to maintain the TN earthing system throughout this installation....
 
Having thought about this abit more the sprinkler system feed is in plastic the goes to steel in the building so no need to bond, so I only have the structure to bond,
the 16mm swa is already in place so can't go for 25mm swa which to be honest is a bit of an overkill for a what is a glorified garage, and a duct is in place to the mains any way so will be easy to pull in a25mm bond

thinking out out of the box here, wouldn't the 16mm Earth core plus the swa armouring combined be equivalent to 25mm??
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Exporting TN-C-S
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
16

Thread Tags

Tags Tags
tn-c-s

Advert

Thread statistics

Created
Suffolksparky,
Last reply from
Leesparkykent,
Replies
16
Views
3,557

Advert

Back
Top