Got to wire up some centeral heating tomorrow. Could do with some advice please.

Need to get a cable out to the garage for the boiler and the frost stat. I'm guessing a 4core for the frost stat and the same for the boiler. There is also a pipe stat to go in, do I need a seperate cable for the pipestat? I'm presuming that the return from the frost stat goes in with the return from the room stat?

Thanks
 
The pipe stat and frost stat are wired in series, basically when the temperature drops below 5 degrees c the frost stat sends power to the boiler, after a few minutes to maybe 20 mins max the pipes are red hot and the pipe stat then shuts the power off even if the frost stat still calls for heat, the frost stat stops the pipes bursting and then the pipe stat stops the boiler running all night on the loop causing high power bills. also 3 cores are usually enough unless the stats are certain digital types, and sometimes a 4 core is needed.
 
I always install a frost stat and low limit pipe stat (on the return of the boiler pipe work) so when the pipe work reaches 20 degrees it will let the boiler turn off regardless of what the frost stat says
The frost stat should always operate the heating valve/ heating side of your 3 port valve or combi boiler (if no frost stat fitted)
 