A AA410 Nov 26, 2009 #1 Here is a good one if you go into your wholesalers and purchese 100 meters of 2.5 twin- earth what should be the r1+r2 reading
Here is a good one if you go into your wholesalers and purchese 100 meters of 2.5 twin- earth what should be the r1+r2 reading
S Sintra Nov 26, 2009 #3 mechelec said: 2.5 with 1.5 cpc 19.51milli ohms per metre gives 0.1951 ohms Click to expand... 0.1951 ohms is the value for 10 M 100M would be 1.951 ohms.
mechelec said: 2.5 with 1.5 cpc 19.51milli ohms per metre gives 0.1951 ohms Click to expand... 0.1951 ohms is the value for 10 M 100M would be 1.951 ohms.