I have a customer who recently had a test an an inspect on his new house. the report showed a high r1+r2 reading on the shed suply. I have checked it out and cant find anything obvious that would suggest why the reading is high on the cpc. however I cant get to a JB that is concealed behind a newly installed kitchen which seems to be the only obvious place the fault can be (the JB apparently is an adaptable box chnaging the t&e to swa, which I reckon is probaly a loose gland on the swa/adaptable box). My suggestion is to provide a earth rod at the shed. the circuit is RCD protected. . . . . thoughts please.
Lurch
Lurch
same as you would any other system, link line and cpc of required circuit at DB and measure at furthest point on circuit if radial, if ring link P1 and E2, P2 and E1 and measure at each socket outlet recording the highest as R1+R2.