Hot Tub troubleshooting

littlespark

~
Staff member
Esteemed
Arms
Supporter
Patron
Ive got a problem with my own hottub. Worked perfectly well for years. Its a Candian Spa hard case type. Not an inflatable lazyspa....

I drain it down properly over the winter, sucking any pools of water out the pipes with a vax.... clean it and refill 2 or 3 times every summer.

Short version... .it is tripping the 32A MCB of the downstairs socket circuit. Board is a split RCD... only the sockets are off the RCD side... lighting is still on straight MCB... as was common when the house was built 20 years ago. Circuits are downstairs sockets, kitchen sockets and upstairs...

Hottub is plugged into an outside socket, which is spurred off a downstairs socket, via a switched fuse, and has its own 10A RCD on the flex. Its on a low load circuit.... not the kitchen. So TV, laptops, wifi router, a few lamps.... i could clamp the circuit cable to see what exactly was being drawn.

But, the hottub is going straight for the 32A breaker... not the 13A fuse in the sw/f. And only intermitantly.... might hold for half an hour or more, then go off again. It has been fins since i unplugged the hottub.


I am thinking its one of the water pumps, and i have not drained the tub for that reason... so i can test it with water in. really, it is just pumps, valves and a heater.

Is there an easy to follow sequence of testing these things that anyone can recommend? I dont want to just start replacing perfectly good parts for no reason.
 
I am thinking its one of the water pumps, and i have not drained the tub for that reason... so i can test it with water in. really, it is just pumps, valves and a heater.

Is there an easy to follow sequence of testing these things that anyone can recommend? I dont want to just start replacing perfectly good parts for no reason.
It would be worth measuring current in the ring to make sure you haven't overlooked a hefty load hidden somewhere and there's no tub fault!

I think to trip the MCB but not blow the 13A fuse puts the fault current around 100 -150A, that would trip the breaker in 40ms, but not blow the fuse, which needs 150 - 200A to blow within 100mS.
That's basically a short circuit (well 1.5 to 2 ohms ish). Wires touching or something.like that. A stuck motor/pump wouldn't draw that much would it?
What, if anything, on the hot tub needs to be switched on for the fault to happen?
 
Last edited:
It would be worth measuring current in the ring to make sure you haven't overlooked a hefty load hidden somewhere and there's no tub fault!

I think to trip the MCB but not blow the 13A fuse puts the fault current around 100 -150A, that would trip the breaker in 40ms, but not blow the fuse, which needs 150 - 200A to blow within 100mS.
That's basically a short circuit (well 1.5 to 2 ohms ish). Wires touching or something.like that. A stuck motor/pump wouldn't draw that much would it?
What, if anything, on the hot tub needs to be switched on for the fault to happen?
i dont know.... it was just the fact that there is some time between trips suggested to me it was part of the pump/heater cycle...

There is nothing high load on the rest of the ring. A lot of things... but nothing huge. TV, laptops, table lamps, chargers... and everything has worked fine since i unplugged the tub.

I think i'll have to plug it in again and wait for it to trip... measuring load while i do it
 
i dont know.... it was just the fact that there is some time between trips suggested to me it was part of the pump/heater cycle...

There is nothing high load on the rest of the ring. A lot of things... but nothing huge. TV, laptops, table lamps, chargers... and everything has worked fine since i unplugged the tub.

I think i'll have to plug it in again and wait for it to trip... measuring load while i do it

You could try swapping mcbs around to at least rule out a faulty one,
 
Any updates? Would be interesting to know what it was?
 
i dont know.... it was just the fact that there is some time between trips suggested to me it was part of the pump/heater cycle...

There is nothing high load on the rest of the ring. A lot of things... but nothing huge. TV, laptops, table lamps, chargers... and everything has worked fine since i unplugged the tub.

I think i'll have to plug it in again and wait for it to trip... measuring load while i do it
The one issue we had with our inflatable hot-tub, which tripped the breaker, was the 'ozonator' ozone generator that is supposed to help decontaminate the water. It's an entirely potted brick with mains flex going in one end, and an air intake pipe and an ozone outlet pipe coming out the other.
If you've got one of those (and you can get at it) - disconnecting its power might be worth a try.
 
i haven't had a chance to look at it yet... and i am expecting it to be a next spring job now. If i leave it any later, i will have to drain it for frost protection
 
i haven't had a chance to look at it yet... and i am expecting it to be a next spring job now. If i leave it any later, i will have to drain it for frost protection

I'd try unplugging the heater wires and running it for a bit, heaters must be the most likely thing to go wrong in hot tubs.
 
I was thinking a breakdown of the heating element when warm causing a short, wouldn't trip the rcd if it was live to neutral, or the rcd doesnt work.
Not impossible but highly unlikely for a heating element to go short L To N.

I think bs7671 recognises that to some degree in 433.3.1

A common cause of element failure is L to E causing the rcd to trip, In the case if a failed rcd (or none at all) the element is unlikely to last very long before going open circuit.
 
Last edited: