Thats the earth fault current so ok now a short circuit fault may be a problem.but with a Zs of 11. 49 Ω, he's only going to get a fault current of around 21A. so the MCB is never going to trip. he;s relying on the RCD for fault protection. the RCD will trip long before the 1.0mm cpc even knows about it. a bit like Pearl Harbour in 1941.we are relying on earth fault protection only.
Not if it meets the volt-drop requirements! What is the PSSC on it?With a High resistance ,& low current on the Live & neutral may be a problem on the mcb tripping.
There was a recent thread on the subject of TT L-N fault protection, in which @Julie. makes some very interesting and valid arguments:Thats the earth fault current so ok now a short circuit fault may be a problem.
With a High resistance ,& low current on the Live & neutral may be a problem on the mcb tripping.