Adding a couple of power points to existing ring main the cabling is Pvc T&E 2.5mm/1.00mm.
Anyone have problems with this, its a TT System,Zs 11.49 ohms.
RCD 30ma...32 amp 60898 B type.
 
I believe the problem with a 1.0mm CPC on a ring final is if it is protected by a 30A rewireable fuse. A fault current high enough to blow the fuse in the required time will mean a thicker CPC is required regarding adiabatic requirements. This shouldn't be a problem for an MCB
 
but with a Zs of 11. 49 Ω, he's only going to get a fault current of around 21A. so the MCB is never going to trip. he;s relying on the RCD for fault protection. the RCD will trip long before the 1.0mm cpc even knows about it. a bit like Pearl Harbour in 1941.
 
but with a Zs of 11. 49 Ω, he's only going to get a fault current of around 21A. so the MCB is never going to trip. he;s relying on the RCD for fault protection. the RCD will trip long before the 1.0mm cpc even knows about it. a bit like Pearl Harbour in 1941.we are relying on earth fault protection only.
Thats the earth fault current so ok now a short circuit fault may be a problem.
With a High resistance ,& low current on the Live & neutral may be a problem on the mcb tripping.
 
Thats the earth fault current so ok now a short circuit fault may be a problem.
With a High resistance ,& low current on the Live & neutral may be a problem on the mcb tripping.
There was a recent thread on the subject of TT L-N fault protection, in which @Julie. makes some very interesting and valid arguments:

 

Reply to Its a trickster... in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
971
OLDBOY
O
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
452
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
710
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock