They all go into fire and all the bells ring regardless of which one I tested. Just the break glass by the front door and rear warehouse roller shutter door won’t trigger the dropping of the lighting contactors. The emergency lights are not affected because there is no interruption to their supply.

that is strange,that would keep me awake all night,so if those 2 mcps trip the panel and all happens as it should would rule out the panel for me,have you allowed a decent time between testing,might be a signal issue,tho the switching off the lights gets me,somethings wrong somewhere that shouldnt happen will cause more panic in a real fire,its not some kind of over ride that should bring all lights on instead of off is it,i could see the reasoning in that.
 
Yeah, plenty of time given for ringing the bells. Everyone in the building can vouch for that…lol
I have given up thinking about it for tonight. It’s fried my tiny little mind.
 
not suprised its a strange one this, think the time delay is down to the smart controller, but other actions are baffling. Good first step as you said disconnect radio links...think thats the only way to start...good luck and keep us all informed,
 
Will do! Thanks for the link Sinlec. I was expecting some phone calls from the office about it today but nothing. Can’t wait to see how this turn out!
 
The info from Simlec was good it shows the fire alarm must be diectly wired to one of the many smart 4 controllers There also must be the main programmer fitted some where. Hopefully the link to the fire panel can easly isolated when found.
 