Hi All,

I have a FCU rated at 1.1 kW (3 speeds) but stating 2.8 A (FLA).

Can anyone explain me what FLA is and why 3.8 A? If I make my maths: 1100 W / 230 V is 4 78 A.

Not sure what I am doing wrong. Thank you.
Mark
 
Can you tell us what you mean by FCU, over here (UK) if often means Fused connection unit.

1.1kW and 2.8A works for 400V but it would be unusual for a single phase load to be connected phase-phase.
 
FCU: Fan Coil Unit.

But also.... apologies... I will try to modify my thread as it's a 3phase fancoil.

Yet...

1100 / (400 * sqrt 3) should be 1.58 A. Not 2.8 A.
Not sure what I'm calculating wrong.
Thank you
 
If you look at motor current charts the FLA does state its 2.8A for a 1.1kW motor at 380Vac.

1640664013789.png
 
FCU: Fan Coil Unit.

But also.... apologies... I will try to modify my thread as it's a 3phase fancoil.

Yet...

1100 / (400 * sqrt 3) should be 1.58 A. Not 2.8 A.
Not sure what I'm calculating wrong.
Thank you

There is also the Power Factor and Efficiency of the motor that has to be taken into account.
 
I think my confusion comes from the fact I don't know the definition of FLA or FLC.

Also, have a look at this picture.
I cannot figure out the maths to confirm the current given once I have voltage, power, power factor and efficiency
 

Attachments

  • IMG-20211228-WA0010.jpg
    IMG-20211228-WA0010.jpg
    38 KB · Views: 67
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
 
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
For some reason I thought that a fancoil only had 1 motor: the fan. But ot seems that this plate differentiates between motor AND fun. Not sure to understand the difference. But if I put some numbers is.... 1.5 kW; 400V; 0.83 eff; maybe a 0.8 PF... we will get more or less the 3.42 A stated.
Also, I can see that my Single Line Diagram only reported the rating of the fan (1.1 kW) but the FLA of the motor it seems.

Question is... if not the fan, what's the motor doing in a Fancoil?
 
The motor converts electrical energy to a rotating force (speed x torque=power)
the fan converts the rotation to a forward flow of air or other fluid.

what are you trying to figure out?
wiring, suitable motor overload etc?
 
There is only one motor, the fan motor.
By 'Motor kW' it means the maximum rated mechanical output power of the motor, as decided by the motor manufacturer.
By 'Fan absorbed power' it means how much mechanical power the impeller absorbs from the motor shaft, as decided by the FCU manufacturer.

So the motor is capable of 1.5kW but the impeller only applies 1.16kW of load to it, leaving a margin so that the motor is not worked to its maximum. However, the full load current is specified for the motor working at 1.5kW mechanical output (P2) and it is a reasonable figure given the rated 415V supply voltage and 83% efficiency (I've taken the power factor as 0.75):
1500 / 0.83 / 0.75 / 415 / sqrt(3) = 3.35A
Which compares well to the stated 3.42A.

With the fan impeller taking only 1.16kW instead of 1.5kW the actual line current will be lower, although not by the factor 1.16/1.5 because only the in-phase current will be reduced, not the magnetising current (and the pf will be lower).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Singapore
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Singapore
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Meaning of Full Load Amperes (FLA)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
Mark_Djorn,
Last reply from
Lucien Nunes,
Replies
17
Views
4,536

Advert

Back
Top