Not the same Cowboy but another cracker: Get a call to house where Central heatings gone down, heating guy took 1 look at it's Electrics & says call the Electrician. Oh joy for me :tounge_smile: Get to house look at boiler supply & go ditch the Power, her ex "Electrician" husband has done the wiring. Found a 1.5 T/E tapped off a radial in the kitchen, this went to a double socket in the Utility room & from the back of this there were 2 Flexes. 1) 0.5mm 3 core feeding the Boiler spur & 2) 1.5mm 3 core flex which went off to feed the Double socket for the washing machine & dryer plus 2 other doubles, from the back of 1 of these there was another 1.5 3 core flex which fed an outside PIR halogen light & went off from there to the Garage. Ripped it all out & re-wired to 1 Double socket & the boiler spur / boiler. Then she says she's been having a little tickle from the Kitchen Fridge Freezer, Plug in loop tester & find No Earth at all. Open socket & it's wired OK so traced the wire to where it went into a spur on the other side of the kitchen, open that up to find the idiot has wired the Earth from the radial into the terminal on the PVC back box & the Earth from the socket to the Faceplate Earth so no path between the 2. Put it back together & checked all other sockets some of which hadd dodgy connections & told her she needs to get some smoke alarms and have the house Re-wired ASAP. Anyone got any Valium ? Lol