Morning all,

I've been tasked with powering up some machinery in a small line plant for one of my commercial clients. I've not done a huge amount of installation regarding motors in the past so it's a learning curve for me.

I'm just looking for advice on whether this set up would work on the attached image (done in paint quickly so not overly detailed) in regards to the emergency stops. These e-stops will be located away from the starters and closer to the machinery and they want a total shut down of all motors in the event of an incident.

My main questions would be;

1. Do the contactors inside the DoL starters have the ability to be controlled by remote e-stops as this would allow me to do away with the standalone contactors I was planning on fitting.

2. Are there any issues with using an independent e-stop circuit wired in series to provide the e-stop function for all 4 motors?

3. Are there any issues with using industrial sockets as the connection point for the motors? I can hardwire them in if necessary but the client would prefer to be able to disconnect the motors from the circuit themselves if they need to take the motors off the machinery for servicing or repairs.

4. In regards to the motor info plates, I assume the amperage on 3ph is per phase?

Thanks in advance.
 

Attachments

  • Screenshot_18.png
    Screenshot_18.png
    44.5 KB · Views: 14
Last edited:
I'm sure you know machinery safety is a regulated area. If not: Machinery Safety Legislation in the UK - https://www.machinesafety.co.uk/compliance/regulations/

If the client's machinery was provided as a complete system by a supplier, there should be documentation/guidance on interlocks and e-stops to help you.

If the installation was bespoke, the designers should ideally be involved.
If your client has put it together, they have the responsibility for following the regs, and should be telling you what to do!

If they are subcontracting design of (even part of) the safety system to you, I trust you are appropriately knowledgeable in the machinery safety standards, and insured!

There needs to be a machine hazard analysis and risk assessment, and that work should reveal what needs guarding/interlocking/ e-stopping etc etc. If that work has been done properly already it should help you with your questions. Documentation is key, as HSE people will no doubt inspect at some stage.

For example - your question on providing connectors on the motors would be answered by hazard analysis/risk assessment
What happens if someone takes a motor out, later someone else turns on the machine - any undesirable consequences or hazards? What is the situation for each motor in turn - do you need the e-stop circuitry to be linked through all the motor connectors to mitigate a hazard etc. etc.

Sorry I'm afraid I can't help with technical details, and if you know all the above already I apologise for the rant!🤪
 
I'm sure you know machinery safety is a regulated area. If not: Machinery Safety Legislation in the UK - https://www.machinesafety.co.uk/compliance/regulations/

If the client's machinery was provided as a complete system by a supplier, there should be documentation/guidance on interlocks and e-stops to help you.

If the installation was bespoke, the designers should ideally be involved.
If your client has put it together, they have the responsibility for following the regs, and should be telling you what to do!

If they are subcontracting design of (even part of) the safety system to you, I trust you are appropriately knowledgeable in the machinery safety standards, and insured!

There needs to be a machine hazard analysis and risk assessment, and that work should reveal what needs guarding/interlocking/ e-stopping etc etc. If that work has been done properly already it should help you with your questions. Documentation is key, as HSE people will no doubt inspect at some stage.

For example - your question on providing connectors on the motors would be answered by hazard analysis/risk assessment
What happens if someone takes a motor out, later someone else turns on the machine - any undesirable consequences or hazards? What is the situatrion for each motor in turn - do you need the e-stop circuitry to be linked through all the motor connectors to mitigate a hazard etc. etc.

Sorry I'm afraid I can't help with technical details, and if you know all the above already I apologise for the rant!
Thanks for the reply Avo.

The client put the system together themselves as it's sort of bespoke to their line of work. They have requested the 2 e-stops in specific locations where users should be operating the machinery but there's no drawings to support this. I was just shown the locations in person/verbally.

As for risk assessments and machine hazard analysis, I haven't been provided with any as of yet. The line plant isn't hands on as such as far as I'm aware, the only user interaction should be starting it all up then letting it do its thing before shutting it down once the process is finished.
 
Thanks for the reply Avo.

The client put the system together themselves as it's sort of bespoke to their line of work. They have requested the 2 e-stops in specific locations where users should be operating the machinery but there's no drawings to support this. I was just shown the locations in person/verbally.

As for risk assessments and machine hazard analysis, I haven't been provided with any as of yet. The line plant isn't hands on as such as far as I'm aware, the only user interaction should be starting it all up then letting it do its thing before shutting it down once the process is finished.
Thanks for the clarification.
I think you need to be careful.
Someone in the client organisation has presumably had responsibility for the machinery 'design', and it would be wisest to seek him/her out, and ask them to provide you with some sort of description of what the company now wants, not necessarily a schematic, even a narrative would do if it's clear and unambiguous, so they are taking responsibility for specifying the new e-stop 'requirements'.
You should persist in trying to seek out what documentation there is already.
 
Adding to the above, and having recently done (but now forgotten most of it) a course on IEC 61508, it's something of a complicated area.
As above, the person/group responsible for the design will need to tell you whether a basic (N/C, open the contacts when pushed) button will do, or whether you need to be employing a safety relay to provide a higher level of supervision of what is presumably a safety function. Again, this leads into whether you can simply interrupt the circuit on the DOL starters, or if you need something else as well.
All this is driven by a hazard/risk analysis for the whole system, and an assessment of the integrity level required - basically, the higher the risks, the higher the integrity level needed for safety functions.

Ignoring those safety questions for a moment, in principle there are several ways to avoid duplicating contactors (a DOL starter is just a contactor with some extra contacts.). BTW, you haven't mentioned whether this is a case of the users simply starting/stopping motors as required, or if there's some sort of control system involved.

So one option is your e-stop circuit controls a relay with 4off N/O contacts - and wire a contact in series with the coil of each starter (i.e. as part of what would normally be an external stop or e-stop circuit.) Hit the button, relay opens, all the starters drop out.

Another option is to control the starters using a separate control supply. I.e., instead of powering the control circuit for each starter from the same supply as its load, separate them. You can then use the e-stop circuit to remove the power from that control circuit and again - open the circuit, starters drop out.
Once you get past a small number of independent motors, it's normal for there to be some sort of control system (even if it's only a few switches and relays in a box) - running from its own supply. Again. for small systems, it's normal for the contactors (and overloads) to be part of the control panel - so one supply, fuses and contactors internal to the cabinet, and then separate cabling out to the motors. So essentially replace "DB" with "control panel" and you've a more normal arrangement for a machine.
 