beaver74

can any one give me some advice about motorized gates is there an average current rating
as i have been asked to supply a motorized gate that no one has seen or even chosen and chances are there will be drive way lighting. at the moment i am calculating 20A over 600m which works out at 50.00mm 3core swa but if loading no were near this a smaller cable can be used
assuming most gates are screw type wich are efficiant.
also as load not constant i would say 35.00mm will work as no heat will build up for 2 or 3 mins it will be in use
 
Surely the best thing to do is tell the client that you are unable to work out the circuit design until you have a firm spec on the gate?

It sounds to me that there are too many variables to guess at this stage.
 
ive only ever fitted one electric gate and it was a few years ago, im sure it was around 700 watts.
 
Maybe best to have a rummage around the net at some suppliers websites and see what general ratings are.

At least that would give you an idea until you get the spec from the client.
 
can any one give me some advice about motorized gates is there an average current rating
as i have been asked to supply a motorized gate that no one has seen or even chosen and chances are there will be drive way lighting. at the moment i am calculating 20A over 600m which works out at 50.00mm 3core swa but if loading no were near this a smaller cable can be used
assuming most gates are screw type wich are efficiant.
also as load not constant i would say 35.00mm will work as no heat will build up for 2 or 3 mins it will be in use
I haven't done the calculations but just looking at your results,it looks like massive overkill.but I'm guessing this was done on a software program,and maybe ambient temperature could be adjusted to help bring down volage drop? Gates I've worked on were low voltage,with a battery back up,but I think only a 5amp supply was needed.I don't suppose the gate is near an electric pole? and you could maybe get a new meter/supply put in.
you could also make it TT and then you could use 2core(a lot cheaper on a 600meter run)
 
Last edited:

Reply to motorized gates in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock