Is the following work notifiable?

Old ring circuit was installed in conduit with singles however when the consumer unit was changed previously some sockets were blanked off because the conduit (earth conductor) was showing high resistance. Obviously previous owner didn't want to spend too much!

Now removed the singles replaced with T&E, and made the circuit a radial, so swopped the MCB to a 20A, and added a couple of sockets in the lounge.

The only reason I could see for making it notifiable is changing the MCB.
 
You are saying that what you have done is:
Replacement of a "damaged" cable with a cable of the same CCC (including the earth?).
Replaced an MCB which is just a switch.
Added two sockets to an "existing" circuit.
Removed a section of unused cable.

So this would not be notifiable.

If what you have done is removed a ring final circuit and replaced it with an extended radial with appropriate CPD.

This is notifiable as a new circuit.

I think you could argue that this is not notifiable but i think it really should be notified as it only matches the old circuit in the positions of the sockets.
However open to interpretation.
 
The design has changed! different cable, mcb changed, installation method changed. circuit type changed.

notifiable,No argument!
 