How would you code this?

  • C1

    Votes: 17 60.7%
  • C2

    Votes: 9 32.1%
  • Other???

    Votes: 2 7.1%

  • Total voters
    28

Strima

-
Esteemed
Arms
There is a poll.

So, one of my lads inspected a street cabinet earlier this week and the cover for the neutral is missing on the DNOs head.

This is accessible by normal persons who hold cabinet keys, they are telecoms engineers but may not necessarily be electrically aware.

I have this as a C1.

My reasoning that this is a TT system so there could well be potential difference between the neutral and earth. It's a big metal box PFC of 1kA and an Ra of 74.3 ohms. PEFC of 0.003kA so a nasty nip could be had.

Unfortunately he neglected to get any continuity measurement between neutral and earth.

The customers in house teams says this is a C2. If it was a TNC-S system then I might agree.

What does the mighty collective say?

IMG_0549.jpg
 
Last edited:
So, one of my lads inspected a street cabinet earlier this week and the cover for the neutral is missing on the DNOs head.

This is accessible by normal persons who hold cabinet keys, they are telecoms engineers but may not necessarily be electrically aware.

I have this as a C1.

My reasoning that this is a TT system so there could well be potential difference between the neutral and earth. It's a big metal box PFC of 1kA and an Ra of 74.3 ohms. PEFC of 0.003kA so a nasty nip could be had.

Unfortunately he neglected to get any continuity measurement between neutral and earth.

The customers in house teams says this is a C2. If it was a TNC-S system then I might agree.

What does the mighty collective say?

View attachment 46386
C1
 
As the neutral conductor is a live conductor essentially what is there is exposed live parts. As you suggest the situation is somewhat more complex with a TN system as this is reliably connected to Earth (however remains by definition a live part - unless it is a PEN conductor as this conventionally is not considered to be a live conductor).
 
C1 for me as it is classed as a live conductor. Only point maybe is that to get in to the cabinet requires a tool or key? By that reason some may consider it an C2?
That was one of their arguments however any engineer with keys can access it but they may not be electrically aware hence my reasoning for a C1.
 
That was one of their arguments however any engineer with keys can access it but they may not be electrically aware hence my reasoning for a C1.
I think I would agree with that as the meter is in there. Had it not been then maybe a C2 could be justified
 
Access to live parts is only possible with the use of a tool. I’d like to think there are signs stating the potential risks and therefore only competent persons should be gaining access to the locked cupboard.
 
when you open its not, safety for some one .

And ai get that but something needs to happen for it to be immediatky dangerous. As in the cabinet needs to be unlocked and opened. There is no way this could be deemed as ‘immediately dangerous’.
 
This is why we can never have nice things as we never agree.

But this kind of debate is good, there are so many variables with this kind of situation there are so many possibilities and outcomes.

So not a C3 then??? :D

As UKPN has pointed out this is DNO equipment and comes under ESQCR but yet on the model forms in BS7671 on the schedule of inspections we are asked to inspect the DNO equipment for faults and report accordingly.

Damned if we do, damned if we don't.
 
There is no doubt that this is covered by BS7671. Only the most irresponsible or lazy electricians would not code this in some way.

My rule is if something needs to happen before it is immediately dangerous then it is a C2.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Strima

Esteemed
Arms
-
Joined
Location
St Neots
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
SS Electrical

Thread Information

Title
Oh goody, a quiz... C1 or C2???
Prefix
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Strima,
Last reply from
stevels4,
Replies
22
Views
3,292

Advert

Back
Top