Got a job to do soon where sub mains x2 have been run to a flat in pyro. Earth via sheath. No gland fitted - just the pot with a BS951 clamp. Suspect it’s all imperial size and tight to access, so not planning to mess about with it too much.
Do these pyro clamps actually exist? Can anyone provide a link for them?
What are my alternatives? I don’t really want to leave the bonding clamps in place as it’s not really correct. I could try and solder a p clip on, but I’m not convinced my soldering skills/iron are up to it. The pyro will act as a heat sink presumably. I’ve only got a cheap thing.
Does anyone know of any sprung/constant pressure clamps that would be suitable? What about a jubilee clip - still a bodge?
Do these pyro clamps actually exist? Can anyone provide a link for them?
What are my alternatives? I don’t really want to leave the bonding clamps in place as it’s not really correct. I could try and solder a p clip on, but I’m not convinced my soldering skills/iron are up to it. The pyro will act as a heat sink presumably. I’ve only got a cheap thing.
Does anyone know of any sprung/constant pressure clamps that would be suitable? What about a jubilee clip - still a bodge?