I wonder how many out there have come across this, and how often.
I was changing some damaged sockets in a flat being refurbed for new tennants.
Of course I always dead test thouroughly before beginning any work.
Twice now I have come across a back feed, by back feed I mean to turn off MCBs one at a time to identify the circuit I will be working on, only to find the particular circuit does not go off unless Two MCBs are switched off revealing the crossed circuits causing the back feed.
One particular one was a radial leg connected into the back of a Spur socket on a Ring, making the whole circuit 32 amp plus 16 Amp making 48 amp in parallel. Scary stuff.
The Other one today, was a Ring where one side was in a 20amp MCB and the other was in a 16amp Radial shared MCB.
It was easy to spot due to the slightly differing shade of Brown covering on the cable, plus verified by testing to define it was a ring.
It was "tested" in 2021 when the new Consumer unit was fitted, so I guess it was swapped then. Whilst its not incredibly dangerous to some, I consider it a C2 that needed fixing ASAP.! Especially as dead testing is not always followed properly by some who trust what the labels say.!
David G1ZQC (Now Retired Aparently) but I still get called out.!
I was changing some damaged sockets in a flat being refurbed for new tennants.
Of course I always dead test thouroughly before beginning any work.
Twice now I have come across a back feed, by back feed I mean to turn off MCBs one at a time to identify the circuit I will be working on, only to find the particular circuit does not go off unless Two MCBs are switched off revealing the crossed circuits causing the back feed.
One particular one was a radial leg connected into the back of a Spur socket on a Ring, making the whole circuit 32 amp plus 16 Amp making 48 amp in parallel. Scary stuff.
The Other one today, was a Ring where one side was in a 20amp MCB and the other was in a 16amp Radial shared MCB.
It was easy to spot due to the slightly differing shade of Brown covering on the cable, plus verified by testing to define it was a ring.
It was "tested" in 2021 when the new Consumer unit was fitted, so I guess it was swapped then. Whilst its not incredibly dangerous to some, I consider it a C2 that needed fixing ASAP.! Especially as dead testing is not always followed properly by some who trust what the labels say.!
David G1ZQC (Now Retired Aparently) but I still get called out.!