Hi, I'm not an electrician but a keen amateur. I understand the testing on RFC and how it's done but couldn't get my head round the (r1+r2)/4 calculation. I've trawled this site (and others) and it seems to me that a lot of people struggle to explain this fully. The truth is that this equation only holds up when the CSA of the conductors are equal - which is not the case with the line and cpc. I attach a document that I think explains it reasonably but I'm sure more experienced professionals can comment (which would be appreciated)
 

Attachments

Having been an electrician for 19 years I can categorically say that the formula is correct.
If I have say 0.30 end to end for my line conductor and 0.50 end to end for my cpc’s (2.5mm T+E) then when I measure at each socket outlet with the cross connection method, then I will measure 0.20 ohms for my R1+R2 measurement.
The calculation/formula is indeed correct.

For same size conductors say 2.5mm then my R1+R2 will be half of my measured r1 ,rn and r2 end to ends, in this example 0.15ohms.
It’s a simple resisters in parallel calculation clearly explained in GN3.

We are splitting hairs here maybe I’ll measure 0.21 at some sockets maybe 0.20 at some and maybe 0.19.

Thank you replying. The way I see it is that there are two formula at play here. The recognised formula for resistors in parallel (1/R=1/R1 + 1/R2) and the derived formula for RFCs (R=(r1+r2)/4). Using your own example of 0.3 r1 and 0.5 r2, the recognised formula gives R as 0.225 ohms and the derived formula gives 0.2 ohms (as you say). This difference is negligible, would be within the 0.05 ohm tolerance and ignored in the real world. However the difference is there. If you take a more exaggerated example, say r1=4 and r2 =12 - the recognised formula gives 3 ohms but the derived formula gives 4 ohms - a significant difference. As "happysteve"says in #23 below " (Q) Does R1+R2 always equal (r1+r2)/4? (A) If half way round the circuit, OR CSAs are equal then yes, otherwise.....well not quite but close enough". That was the point if my original post.
 
Yes, half way round the ring is the worst case - and that's what matters for fault protection etc. Anywhere else on the ring will have a lower value - as demonstrated by the graph posted (whichever way up you look at it) :p
The different lines on the graph are irrelevant. The deviations from the simplistic formula only occur away from the centre point of the ring - where the resistance is lower than the worst case anyway.

But for a simple explanation ...
Consider a fault at the midpoint of the ring. From the MCB in the CU to the fault, you have two equal conductors in parallel - each of which is half the length of the ring and hence has half the resitance of the whole ring. So you have two resistors of value r1/2 in parallel, and two equal resistors in parallel give you half the value of each of them. So you have (r1 / 2) / 2, or r1 / 4.
The CPC has the same calculation, so from MET to fault you have r2 / 4.
So total is (r1 / 4) + (r2 / 4), which is better written as (r1 + r2) / 4
Again, this is the worst case, at any other pointbround thecring, the total resistance to the fault will be lower. So you don't need to considervthe effects of different line & CPC sizes etc. This even hold true if the cable CSA changes round the ring IF you consider "middle of the ring" to be in terms of cable resistance rather than distance.
It would be a diffetent case if the CSA variations were "odd" - eg if in one leg you had a larger line, and in the other leg you had a larger CPC. But that would be unusual !
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
(r1+r2)/4, the myth expelled?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
KeenPensioner,
Last reply from
static zap,
Replies
48
Views
5,746

Advert

Back
Top