i tested a ring final circuit today. the installation is steel conduit and 2.5mm conductors L-N-E

i got 0.56 for r1 , 0.54 for rn and 0.21 for r2

is the steel conduit naking my resistance lower, id say without a doubt but somone keeps saying they should all be the same,,, thanks trev
 
so would you say the steel conduit is making this reduce to 0.21... just asking ... he making me doubt myself
 
Just think what the csa of the conduit is compared to a 2.5 or 1.5 copper conductor.
 
Yes it will be, just think every switch and socket plate will probably be connected to the steel back via a fly lead.
 
it is and i walked outa work, cause i couldnt work out somone wire a lighting circuit with fans and sensors on, done me head in, boss said dont worry we gonna rewire it, see ya in morning.. and what a day
 
does line and neutral need to be in same conduit, i would say yes but what about switchwires and the like
 