shocked
Hi all
testing the lighting circuit in this flat 5 lights, 15/20 year old pvc/pvc all ok but the r1+r2 readings are too high last light is 3.59 ohms zs at last light is 0.86 ohms ze is 0.15. The r1+r2 on the cable to first light was what i would have expected but from then on got higher and higher. I checked all the connections at the pendants , just could not seem to find out why the were high but my zs was ok.?
thanks
john
had a similar thing happen to me turned out to be dodgy connection in test leads tested again with new leads was all ok (did you null leads before test?)
did you test the other circuits in the flat and were your readings ok does seems a strange one
hi shocked had exactly the same problem yesterday on a lighting circuit,have you tried testing R2 + Rn or R1 + R2 to the feed side of the pendant and not the switch side to see if you get the reading youre expecting, if youre getting the right readings from them tests try your light switches thats where my problem was put connector block to temp bypass the switch and all readings where then fine, this happened on about 3 out of 5 lights i tested
i would be inclined to go with crow11 on this. resistance of switch/es.
I agree with crow11 and telectrix - high resistance in the switches. I bet they are cheapos!
I wouldn't disagree, but i also wouldn't rule out a loose connection. Once had a very high r1 on a ring of about 200 ohm, half a turn on a terminal screw in one of the sockets got it down to next to nil. There is not much difference between a good and bad connection, especially in pendants, when the biggest driver you can get in is usually a terminal driver.
Cheers............Howard
Good point SirKir Breaker. It's one of the reasons that on power circuits I like testing R1+R2 with the accessory unscrewed rather than through a test plug. That way if there is a sudden increase it's off the wall and ready for a bit of attention.