S
Sck
Received with thanks
What's going on?
All you need to do to find R2 is multiply the length (30m) by the resistance per metre of whatever csa you are using.
you may not yet know the size of your cpc yet for design purposes , but if you know the load size and circuit length , you can select your phase conductor size , which will give you R1
No need to involve Ze or Zs.
in fact, Zs cannot be determined until after you have calculated R2 (and R1)
again for the purpose of design calcs , you use the max Zs allowed for the chosen circuit device to help determine your minimum cpc size.
Yes, I did get lost but this thread does seem to be rrrr about face.
Shouldn't the equation be -
R2 (mΩ/m) = ( Zs - Ze ) x 1000 - R1(mΩ/m)
. . . . . . . . . . .( length x 1.2 )
R2 = (Zs - Ze) x 1000
(L X1.2) - R1
R2 = (3.83-0.4) x 1000
(30 x 1.2 ) - 7.41
...
Zs = 0.4 ( (7.41 + 18.10) x 30 x 1.2 )
1000
= 1.32 Ohms
Ok. I read the wrong figure.you've used 1.32 for Zs , the op gave a figure of 3.83.
No, i didn't actually do it but that can be done for whatever value of R1 is chosenhave you deducted the R1 of 7.41 he gave in the 1st post ?
The resistance values are the same.the cable described was pvc singles , not t&e.