Hi all.
I'm having a discussion with a customer. I have been fitting out camper vans for over 8 years now and have always used double pole breakers or RCBO's. with a Main switch MCB
This customer says I can fit a small 2 way unit with just RCBO's and there is no requirement for a Master MCB?
I know we should not argue with safety, but he has got me doubting myself, what do you guys n gals think?
 
Hi all.
I'm having a discussion with a customer. I have been fitting out camper vans for over 8 years now and have always used double pole breakers or RCBO's. with a Main switch MCB
This customer says I can fit a small 2 way unit with just RCBO's and there is no requirement for a Master MCB?
I know we should not argue with safety, but he has got me doubting myself, what do you guys n gals think?
I am guessing no one knows the answer? Reading my 18th edition, its just states a device to isolate both phases! Anyone?
 
462.1.201 A main linked switch or linked circuit breaker shall be provided as near as practicable to the origin fo every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single phase supply.


When you say, "a main switch MCB", presume you mean a double pole MCB?

I wouldn't necessarily say you need a (double pole) MCB up front (for overload and fault protection) - the supply will be protected and limited upstream - but you certainly need a double pole "something" to comply with 462.1.201.


There's also a specific reg in Section 721 about this:

721.537.2.1.1: Each installation shall be provided with a main disconnector whuch shall disconnect all live conductors and which shall be siuitably placed for ready operation within the caravan. In an installation consisting of only one final circuit, the isolating switch may be the overcurrent protective device fulfilling the requirements for isolation.

So there you have it, in black and white, in the Regs. If one circuit, then fine, an RCBO with switched neutral is sufficient. If more than one circuit, you also need a main switch.

(Do you have a copy of the Regs? You could show it to the customer, it'll probably carry more weight than a random post on the internet by someone called "happysteve")
 
462.1.201 A main linked switch or linked circuit breaker shall be provided as near as practicable to the origin fo every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single phase supply.


When you say, "a main switch MCB", presume you mean a double pole MCB?

I wouldn't necessarily say you need a (double pole) MCB up front (for overload and fault protection) - the supply will be protected and limited upstream - but you certainly need a double pole "something" to comply with 462.1.201.


There's also a specific reg in Section 721 about this:

721.537.2.1.1: Each installation shall be provided with a main disconnector whuch shall disconnect all live conductors and which shall be siuitably placed for ready operation within the caravan. In an installation consisting of only one final circuit, the isolating switch may be the overcurrent protective device fulfilling the requirements for isolation.

So there you have it, in black and white, in the Regs. If one circuit, then fine, an RCBO with switched neutral is sufficient. If more than one circuit, you also need a main switch.

(Do you have a copy of the Regs? You could show it to the customer, it'll probably carry more weight than a random post on the internet by someone called "happysteve")
Thank Steve. I do have my 18th Edition.
My point to the doubter was if only one circuit an RCBO is suffice, but for 2 separate circuits then a Master Switch is required to break the feed to both circuits for isolating. I do mean a DP MCB.
Thank you.
 
Yes you would need some means of single point isolation.
 