Can you get away with a rcd incorporated fused spur unit / or socket?
depends if cable is in the wall
Can you get away with a rcd incorporated fused spur unit / or socket?
so what if the cable was buried at a depth greater than 50mm...and/or was given additional protection by earthed metallic conduit....?....If the socket is behind the appliance and unlikely to be used for anything else then no rcd required.
If cable is buried in wall then rcd needed anyway.
Bathroom dimmer ok if outside zone 2.
so what if the cable was buried at a depth greater than 50mm...and/or was given additional protection by earthed metallic conduit....?....
of course....no probs Biff...We both know the answer to that Glenn lol.
Yes the sheath of FP cable is made of metal and is in contact with the protective conductor, so as long as you have connected the CPC correctly the sheath of the cable is earthed.Is the sheath of FP200 classed as a "earthed metallic sheath"?
In terms of it being an earthed metallic sheath then, in my opinion, yes. With MI and SWA you have to connect the sheath to earth which is not required for FP as it is already connected to the CPC.Never thought of It like that...
Would that comply in the same way as MI and SWA then?
well if its touching throughout....would you say thats a better arrangement than if it was just connected either end....Yes I see thanks.
My only concern was that it is not connected either end. Just touching throughout.
well if its touching throughout....would you say thats a better arrangement than if it was just connected either end....
wire it in fp200 or similar earthed metalic sheath?
afraid i must disagree with the use of FP negating the need for an RCD. my reasoning is that the flimsy bacofoil cable covering does not comply " with the requirements of the regulations for a protective conductor........" ( reg. 522.6.6 (i))