Evening , got to wire in a smeg 19.5kw
Total load 84.7
Diversity: 10amp
30% of 74.7= 25amp
Total = 36
I would fit 40-45amp breaker on 10mm clipped direct. No insulation and no cooler socket ?
Am I missing something with Smeg and why they want 53 amp. Tried to contact them but no joy as yet ?
Thanks
TR4110IGR
Using diversity I work it out to :Total load 84.7
Diversity: 10amp
30% of 74.7= 25amp
Total = 36
I would fit 40-45amp breaker on 10mm clipped direct. No insulation and no cooler socket ?
Am I missing something with Smeg and why they want 53 amp. Tried to contact them but no joy as yet ?
Thanks