TN-S is the manner in which your earth is derived but it may well be connected from a PME system in the street. I suspect that notice is there for the benefit of EV charger installers whereby if a TN-S earth is derived from a PME system it is not "pure" TN-S for the purpose of the charger.
Never seen a sticker like that before but makes sense if what looks like an old lead sheathed cable into the property, with the lead sheath being the earth conductor hence TN-S at that point.
All TN-S systems must now be considered TN-C-S for safety reasons. There are far too many and increasing examples of work done in the road to repair cables and the lazy installers bond the earth to the neutral in the torpedo. It has ruined the safety of many domestic streets and led to numerous safety issues and electricians being shocked. It's why clamp meters are now recommended parts of safe isolation procedures (I worked with one Housing Association who gave everyone earth-leakage clamps and made it a disciplinary matter if if we're not used during safe isolation).