Engineer54
In effect the rod has become an extraneous-conductive-part, that requires bonding back to the MET in the house.
This will require a minimum 10mm² copper bonding conductor.
There is absolutly no reason why you can't connect a good earth rod electrode to a PME installations MET!! In fact most European PME Regulations, Require a Rod electrode to be present at the installations MET... No reason why you shouldn't have a Rod or electrode at a TN-S MET either, in fact on most of the old council house estates of the 50's that's exactly what was provided...