J james1 Sep 3, 2008 #1 hello i am changing a distribution board in a flat. the pfc is 6.3 ka can i get away with type b 6ka mcbs have them all ready or would i have to use type c 10 ka mcbs thanks
hello i am changing a distribution board in a flat. the pfc is 6.3 ka can i get away with type b 6ka mcbs have them all ready or would i have to use type c 10 ka mcbs thanks
T tony.towa Sep 3, 2008 #2 The 6kA breakers are not capable of withstanding the prospective fault current so you need to use the 10kA breakers.
The 6kA breakers are not capable of withstanding the prospective fault current so you need to use the 10kA breakers.