Those CT's are poorly installed as well. Laying them on top of each other will negatively affect the accuracy. Also I don't like seeing CT's unsecured. It's not so much an issue with small supplies but with commercial/industrial installations there can be very large mechanical forces involved, especially under fault conditions, that would cause the CT's to be propelled in unexpected directions. At worst these forces can be strong enough to cause the CT's to disintegrate if they're not adequately anchored, at best the secondary wiring can be damaged or disconnected which can cause overheating.