I agree Trev, thats how I`ve always understood the rule, no more than 1 spur from either a JB, socket or CU
 
Last edited by a moderator:
Not sure. It would makes sense from a practical point of view,but can't find it in black and white and I can't see how it will effect the loading on the terminals which will still be protected to 32a?

Interested to find out though.
 
I agree that it's 3 separate spurs but aren't you allowed 1 spur from 1 point of utilisation?
If you can find it in "the book" you are a better man than me.It's beside the point really, none of us would do it because we are not lazy good for nothing thieving scum bags like the people that carry out work like this.
 
It's a Pig's Ear of a job, and that's an end to it!!! How are you going to substantiate that kind of connection or circuitry?? You Can't!!
 
i run a 10 ml circuit for a shower and it was changed to a double socket and the 10ml fitted the socket . . . and no it was not in a bathroom
 
what would you note on a report what code would you give it. Because its not a spur off a spur the cable should not get overloaded, but somewhere it says one spur from each outlet, is there a reg on this?
 
yer some are ok must most of the jobs iv seen are poor quality and always have remedials after its completed.
 
ok its rough as a badgersd we are agreed on that

if you can Id fit a F.C.U. beside existing socket and take the mess from load side of FCU not a "proper job " but better and safer than pigs ear that sausage rolls left
As for finished walls they will need refinishing if it catches fire Explain to him Why its wrong and the possibilities to make it safer and get him to SIGN for work being carried out in your cert Put that this was work done previously and not by your self and make sure you have EXACTL:Y what you have done as they may have other things unsen as yet
 
Check appendix 15 fig 15A of the BGB regulation 433.1.103 this may help to sway your customer to do the right thing
 
When training I was taught, we can add as many unfused spurs as there are existing socket outlets on the RFC but, only one from each point be it JB, CU or existing socket.

RFC theory tells us that spurring 4 or 5 outlets from one socket is asking for trouble as the shortest leg of the RFC feeding that socket outlet with the 4 or 5 spurs connected to it, will have it's (Iz) exceeded at some point as the loading will be significantly higher at that point.
 
When training I was taught, we can add as many unfused spurs as there are existing socket outlets on the RFC but, only one from each point be it JB, CU or existing socket.

RFC theory tells us that spurring 4 or 5 outlets from one socket is asking for trouble as the shortest leg of the RFC feeding that socket outlet with the 4 or 5 spurs connected to it, will have it's (Iz) exceeded at some point as the loading will be significantly higher at that point.

Lenny is our hero, Lenny is our hero, la la la:party::party:
 
When training I was taught, we can add as many unfused spurs as there are existing socket outlets on the RFC but, only one from each point be it JB, CU or existing socket.

That was a common method of wiring small 2 up and 2 down terraced houses!! ...lol!!
They spurred off the ground floor sockets straight up to supply a bedroom socket, where required. Iv'e even seen some rings, where every socket was spurred off the main ring via JB's...lol!! Both perfectly compliant, both then and now, but not perhaps the best methods of wiring a RFC !! ...lol!!
 