701.411.3.3: "Additional protection shall be provided for all low voltage circuits of the location, by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1."
I don't really see that the Regulation is ambiguous, or can be interpreted other than as a requirement to provide RCD protection.
As the work proposed involves an alteration to the fixed wiring to a circuit of a location containing a bath or shower, in order for the alteration to comply, the whole circuit must be provided with RCD protection. Not just a part of the circuit by means of an RCD FCU.
 
Great debate and a few people shooting me down in flames (which I deserved).

The alternative for installing an rcd which I thought of from the start and no one has mentioned yet:-

From the original hard wired circuit, install a transformer able to supply all 5 lights and spider off to each. Selv has then been provided out of zones in the loft and no rcd is needed.

But of course we all would install a rcd because we all know its the safest way. Just liked the debate, that's all gents.

Can I take my tin hat off now? :)
 
I must admit there is quite a number of sparks think that if you do a minor works on an installation It can be to the same regs as when it was installed , no regulations change and the changes have to be brought in to existing installation and new so minor works to current regulations special locations also have to be notified , so this installation although minor would have to be done to current regulation so requiring an RCD
 
I must admit there is quite a number of sparks think that if you do a minor works on an installation It can be to the same regs as when it was installed , no regulations change and the changes have to be brought in to existing installation and new so minor works to current regulations special locations also have to be notified , so this installation although minor would have to be done to current regulation so requiring an RCD


Nice, so does this mean I can do CU installs on a MWC and not bother about bonding etc?? lol
 
Paul m
You won't get anyone state the reg as there isn't one
The word interpretation is magical that's why them people who wrote the regs use it

there is this one
701.411.3.3

oh see it has been mentioned already doh
 