R
revolt3k
Turn up to an old ish house to do a normal C.U upgrade. One of those where 1 fuse for the ring up and down, one for all the lights, one for cooker etc. So around 4-5 circuits in all. so after isolating etc i do a quick IR of all circuits connected with eveything removed or if there is loads of transformers on DL's i do L-N to E. Anyways 35M ohms so that looks good. Start with the ring, in the 30A Fuse were 3 cables. So normally 2 would be the ring and the other a spur to a socket close by or somthing simlar. I did end to ends to get nothing?? So i had a look aroud for any new alterations etc but couldnt see anything obvious. Started to take fronts off and figured out where the cables went etc. After many hours it look like it used to be a ring but some cables were cut off and left dead? So by the look of it the 3 cables were 3 raidels on a 30A
Whats the best way to figure out what should and shouldnt be a raidel? All the wasted time :(
Hi Revolt
Bit of a sod when you get that ! best way is discon all sockets and start with first on cable 1 and note A on cable in cu then find 1st socket and write A1 on it then add outgoing on that socket and find what socket is next and A2 and so on till no more on that circuit then go to cable 2 in cu and write B on that and so on onece you know what goes where you can convert to 1 x ring 1 x radial etc ! time consuming but works.
Hope this helps
Regards
Kung.
Thats exactly what i ended up doing mate. Would you have thought about making it back into a ring? Im happy with them being on 20A MCB's as radials but it was a nightmare trying to figure it out. You come accross many of these?
Lots m8 and their all a pain
"Character Building" jobs are what keeps us thriving!
I'd rather have troubleshooting / faultfinding than the monotonous day-in-day-out routine bread'n'butter stuff... that's why I'm a raggedarsed factory spark, perhaps ;)
Regards
s.f
