daz1963
just been to quote for a added socket. nice new 17th edition board, so thought all should be ok. quick check of efli gives me a zs of 2.2ish ohms.same on a few more sockets. so goes to main board and checks ze,which is 1.9 ohms. a tad to high for tn-s at 0.85. now if this was a tt system that would fine. as its a tn-s would you contact the dno to rectify it? or would you leave alone and add the socket as its rcd protected? i will ring the dno and see if i get anywhere with them which i doubt.just wandered what anyone else would do.now be honest:wink5: