would it not be better to have there own transformer with tns on the secondry side? than spending 30k on rod installWhy does an IT system need a functional earth RA of less than one ohm?
Last edited:
would it not be better to have there own transformer with tns on the secondry side? than spending 30k on rod installWhy does an IT system need a functional earth RA of less than one ohm?
@ UKSparks, I'd suggest rather than spending 30 pounds per earth pit you might just use a length of plastic drain and cut a slot each side for the wire coming in and going out. You get 225mm PVC pipe and end caps (8-inch in old measurements), you could make numerous rod covers from a single length of pipe.
You made me get the drawing out now lol.
There in fact 21 (I missed one) dotted around the building They are roughly 7-10 meters apart depending on basically where it was convenient to site a pit. I wanted to get each rod approx valuation of between 10-15 ohms.
The 70mm conductor is not cheap I agree but I spec it as I needed to hit that 1 ohm target. I was thinking of using some lightening tape but I decided against that as the conductor lays bare and I wasn't sure how it would react in the soil.
I have yet to find any sort of realistic calculations on getting the "right" results for this. I guess you can take soil resitivity and conductor sizes etc, but the bottom line is suck it and see. I may have been able to get away with 50mm conductor, but it it hadn't worked, then there is a lot of red faces on the site, especially mine lol
Jeeees, thats a lot of money!
blimey 3/4 rods too!!
Well ideally I would like to get a sub 1 ohm, but will see, its only a large summerhouse thing, but I would rather not accept 200ohms, I banged a rod in my garden last week, two 5/8 rods connected end to end and got 42 ohms, I think with 6 I might stand a fair chance of getting a good reading, but who knows! Ill find out in the morning.
The cost does start to creep up indeed, the pits are the best part of £30 each, so its a little hard to explain to the customer I need the best part of £100 of concrete pits when they don't even understand what a rod does.
would it not be better to have there own transformer with tns on the secondry side? than spending 30k on rod install
I imagine it would be pretty tough to explain away 8x earth rods with concrete pits and 25mm earth cable for a summer house, whats the point in that????
bit OTT innit
Ok, so if you have one rod of say 20 ohms, the reading will be 20 Ohms ok..
So suppose, I have two rods in to the ground both reading 20 Ohms, and link them together, what will the resistance be then? Does it work the same like if you were to IR a whole board, taking parrallel resistances into it etc?
What I am trying to work out, is if I have say three 20 ohm rods, hook them together, whats the end result and how do I work that out? Presumably there must be a calculation for this?
the earth will settle to the rod in time.
View attachment 29117
It is a functional earth for data and our remit was less than 1ohm, so pretty pleased with that
the building is at least 200M parimiter so its not small and multiple floors as well i imagine, im guesing the rods are for a supply tx and might be feeding external buildings as well we don't know.I ask what system needs a functional earth of 1ohm?
IT systems and data centres require low imp earthing for comms earth references, many comms systems use a very low voltage carrier so even small potential differences across reference points can lead to problems. Also for effective operation of surge and lightning protection, a low impedance earth prevents a rise in potential during their operation which is especially important if there's remote assets. Also for effective screening of cabling etc. The earth for these installations is highly functional as well as its usual protective role.I ask what system needs a functional earth of 1ohm?
Ok, so if you have one rod of say 20 ohms, the reading will be 20 Ohms ok..
So suppose, I have two rods in to the ground both reading 20 Ohms, and link them together, what will the resistance be then? Does it work the same like if you were to IR a whole board, taking parrallel resistances into it etc?
What I am trying to work out, is if I have say three 20 ohm rods, hook them together, whats the end result and how do I work that out? Presumably there must be a calculation for this?
I ask what system needs a functional earth of 1ohm?