A
assegayer
Hi guys,
really need help to solve this question i have on my assignment for my apprenticeship not asking for the answers but for guidance page numbers etc
Basically after cable cals i got 4mm2 for live conductors for one of the circuits they wanted me to work out and it is a 36m length run.
I know that i need to find the fault current and to do this i need r1 and r2 values i think? where do i get them from in OSG or regs?
also the the equation requires a disconnection time or something like that.
I would love some help, thanks guys
Hi guys,
S=√I²t/K
AMD3 OSG Appendix I (page 189) for Resistance of conductors.
It will be (R1+R2) also mate. The smaller case refers to ring final circuit end to ends.
Once you have calculated the Ipf compare it to the graphs in BS7671 appendix 3 for the disconnection time.
Hi guys,
Appendix I Table 11
The adiabatic equation is given in reg 543.1.3. Values of K are given in tables 54.2 to 6. The time current characteristics of OCPD's are found in appendix 3. You need to know the fault current this can be derived from V/Zs. You can calculate Zs from the length of circuit and Ze.