Are these general use sockets or are they intended for specific appliances?
16x 13A outlets spread across 3x 32A ring circuits seems well provisioned for general use outlets
They are all general sockets. 8 x 2 port 13 amp. But it's more to do with the layout. The list of equipment detailed 4 main items along with a few other peripheral devices. A grill and three hotplates. A total of 50 amps for those items alone. I would have liked to see dedicated outlets for these 4 devices with their own single 64 amp MCB and circuit. At this point in time there is nothing to stop someone plugging 8 x 13 amp devices into one of these segments while it only has a 32 amp MCB. You can't expect the end user to know the dangers of doing so. The layout should be designed to prevent it in my opinion. As far as is reasonably possible at least. If you tskr this to its extreme it is possible to demand 208 amps from the CU through three segments each with a 32 amp MCB.