Manufacturers specify a maximum earthing resistance for their RCBO's, this may not always be met with TT systems.

For example schneider specify a max earthing resistance of 100 ohms.
 
There was and is a requirement to disconnect all live conductors for a circuit protected by an RCD

And now they have rigged the rejigged the regs to allow single pole RCBOs
Can you point me to it. Are we talking rcd or a circuit protective device such as an rcbo.
 
I am talking about RCDs but in doing so that also includes RCBOs and other such devices
I am talking rcbo, there is no requirement for them to disconnect the neutral on a TT system where their function is only circuit protection.
 
Manufacturers specify a maximum earthing resistance for their RCBO's, this may not always be met with TT systems.

For example schneider specify a max earthing resistance of 100 ohms.

Hager used to stipulate no sp RCBOs for tt systems and now it’s all ok..
Why?
Because it suits what they are selling
 
There was and is a requirement to disconnect all live conductors for a circuit protected by an RCD

And now they have rigged the rejigged the regs to allow single pole RCBOs
If they have rejigged the regs, they did it back in the 1980s.
 
Hager used to stipulate no sp RCBOs for tt systems and now it’s all ok..
Why?
Because it suits what they are selling

Or maybe they have changed the design of their RCBO's to be suitable for use on a TT system.

I don't fit Hager so I don't know, do they have functional earth's for their RCBO's or are they the type without?
 
For years I have used dp RCBOs on tt systems - MG or Hager and will carry on doing so..
Seems strange that the regs are ok with not disconnecting the neutral on a tt system even though it’s not tied to earth.
 
It stipulates RCDs shall disconnect all live conductors for the protected circuit except for protection against electric shock
 
If we need double pole protection in TT installations, then fuses can’t be used.
So we have to condemn all those BS 3036 and BS1361 fuse boxes.
What about the DNO fuse, or plug top fuses?

Wait, what about single pole light switches?
 