Does anyone have a suggestion re providing short circuit selectivity to a sub-main? Overcurrent and Earth Leakage aren't an issue, but in my experience, standard MCBs have a 50/50 chance of either tripping the breaker in the sub panel or in the feed.

My normal approach is to use a fuse, but I wonder whether I'm overlooking any re-settable options?

Thanks,
 
As you observer, if you hit the magnetic trip limit of the upstream MCB then usually both trip, and often that is easy to do (e.g. 50A B-curve might go at 150A PSCC). If you want good selectivity and user-re-settable action then go for a MCCB that has a short-term delay (typically 20ms) up-stream of and MCB boards. Typically that will give you a good kA or two of selectivity and if that is above the final circuit PSCC then job done.

If you don't want the cost of MCCB and it is an unlikely-to-fail circuit then a fuse has a lot to recommend it. Cheap, reliable, and very good energy-limiting on major faults.

If you looks at the catalogues of the more professional brands of suppliers then they typically have tables of selectivity with fuse/MCCB/MCB upstream and MCB/RCBO/AFDD downstream to see what sort of combinations are going to be acceptable.
 
Download the Hager commercial catalogue (14MB PDF document) from here:

Selectivity tables are from pages 142 to 151. Examples of feeding a 32A B-curve RCBO from 50A upstream OCPD are:
  • 50A NBN B-curve MCB = 0.22kA
  • 50A NDN D-curve MCB = 0.69kA
  • 50A x160 series MCCB = 1.03kA
  • 50A BS88 fuse = 1.10kA
 
Thanks both. Shame nobody yet has any offerings in the "domestic" price range. Guess I'll have to stick to melty wire for the time being :)
 
Thanks both. Shame nobody yet has any offerings in the "domestic" price range. Guess I'll have to stick to melty wire for the time being :)
Fuses are good, just not for non-specialists to replace safely.

Another aspect in their favour is generally they can be used with higher Zs than MCCB/MCB for a given operating current. For example (at working temperature, not including typical 0.8 factor) we have for 5s sub-main on TN the following Zs values:
  • 50A B-curve MCB = 0.87 ohm
  • 50A D-curve MCB = 0.44 ohm
  • 50A Hager x160 series MCCB = 0.44 ohm
  • 50A BS88 fuse = 0.99 ohm
TL;DR the fuse has best selectivity and highest Zs of the common (and affordable) options. Obviously you can use a MCCB with earth leakage option to meet higher Zs along with good selectivity on overload faults, but it will cost you (or the client!) a pretty penny.
 