Hi all @ef.net, I'm a newbie to the forum; this is my first post. The Danfoss FP715si programmer that had been in use for about 8-9 years began to malfunction (so it seems).
Although the programmer is programed and had functioned normally, it has begun, also, to operate randomly outside of the programmed timings. Some checks/maintenance had been done beforehand : checked 3 way valve operation, bled rad's and pump and checked that programmer was operating in accord with set timings, then along came those 'extra' random, unprogrammed operations - wake up in the middle of the night in a sweat!
If the consensus is that the programmer is bust, I could buy a replacement from plumbvent.co.uk (anyone used that Co?)
Any advice and ideas very welcome.
Regards Lojong777
Thanks re. the 'sticking-in' buttons tip; none are sticking-in. Will do voltage checks, soon, on the 3-way valve through its switching sequences + contacts in HW & Room stat's and at boiler and pump and so on! A curse on Benjamin Franklin and his kite.
There is a recent thread on here concerning this programmer.
There's a capacitor inside that drops the voltage that the electronics run down from 230V down to something more suitable. This capacitor can slowly fail over the years, until the programmer starts to give problems.
Note that is must be replaced with a X1 or X2 at worst version.
Hi, Not clear on the meaning of
....... 'must be replaced with a X1 or X2 at worst version'.
Class X capacitors are safe to connect across line and neutral. Class Y are safe to be connected between line and earth. It's vital to replace with similar types to avoid fire hazards.
Been busy so only just concluded that my faulty programmer sends a constant voltage to term. 4 on the terminal bar, the CH 230V input to the room stat'. Hence, the CH timing is overridden and unless the room stat' is turned down, the boiler continues to cycle 'forever'. Probably look for an alternative to Danfoss - any suggestions for a good 'un'?
Is the display operating correctly? Can you toggle it on/off with the 'Man' button? Does the red 'heating on' LED go on/off at all? If the screen is playing up it could well be the dropper capacitor as in the other thread. If not then my next suspect would be the relay. I've got the repaired unit from the other thread here that I could send to you for the cost of the postage and the repair part that I fitted. Call it £4.50? Up to you. If you do want to swap to an alternative to Danfoss, the Drayton LP722 is a direct replacement.
Hi Moley
Many thanks for your generous offer re Danfoss. As my system controls are decades old, I decided on a fresh start. I have ordered a Drayton LP112 programmer and RTS1 room stat'. If I had seen your post before I had ordered, I would have looked at the Drayton LP722.
With best wishes
Hi Moley
Many thanks for your generous offer. My present programmer and room stat are decades old, so I decided on a fresh start and ordered a Drayton LP 112 and a Drayton RST1 room stat. I would have looked at the Drayton LP722 had I not already ordered.
Best wishes
Hi Moley
Any chance of you sending me the faulty unit to strip down and fault find? If you can send it let me know if you have a Paypal account and I'll send you the postage.