Part P / Part F

Recently i have a client who claims i need to register with building control and commission his extract fan.
The fan is installed outside all zones in the bathroom, from the lighting circuit and spured down to 3a.
I have read part F and Part P and the way i understand it is this is not a new circuit from the consumer unit, its outside the zones and a minor works cert with all test results is valid.
I am with the NICEIC and have asked for their advice but they can take days to reply. I am not training to commission extract fans and i wasnt aware i needed to do this. The fan is running on humidity, envirovent infinity 8.
I want to be compliant with regs and building control but i felt i was. If i have installed a new circuit or changed the consumer unit this would have been notifiable to NIC for a building control cert.
 
Recently i have a client who claims i need to register with building control and commission his extract fan.
The fan is installed outside all zones in the bathroom, from the lighting circuit and spured down to 3a.
I have read part F and Part P and the way i understand it is this is not a new circuit from the consumer unit, its outside the zones and a minor works cert with all test results is valid.
I am with the NICEIC and have asked for their advice but they can take days to reply. I am not training to commission extract fans and i wasnt aware i needed to do this. The fan is running on humidity, envirovent infinity 8.
I want to be compliant with regs and building control but i felt i was. If i have installed a new circuit or changed the consumer unit this would have been notifiable to NIC for a building control cert.
Competent person schemes (such as NICEIC or NAPIT) often require specific ventilation certification or an additional ventilation scope on top of standard electrical registration to sign off on fans.
 
Competent person schemes (such as NICEIC or NAPIT) often require specific ventilation certification or an additional ventilation scope on top of standard electrical registration to sign off on fans.
i am not part of a ventilation scheme and have no training in ventilation commission, you need to know natural air flow and be trained to complete this.
 
Seems you have answered your own question.
i spoke to NICEIC today and they told me extract fans are not subject to notifiable works when not in the zones of a bathroom or part of a new circuit from the consumer unit. So it seems odd that we dont notify for the install but building control needs the commissioning form
 
From memory. Electrically there's no notification requirements as described.
But there's now rules about extraction systems - minimum airflow and the like. You can't just bung a fan through a hole in the wall, there's a pile of compliance stuff to deal with.
 
Competent person schemes (such as NICEIC or NAPIT) often require specific ventilation certification or an additional ventilation scope on top of standard electrical registration to sign off on fans.
That's the reason so many sparks get frustrated with these schemes, a ventilation certification to sign of a bathroom extract fan, not a full blown laundry. or such with dampers and actuators linked to the F/Aalarm system... just a 100mm bathroom fan . We are doomed I tell you.... doomed
 
That's the reason so many sparks get frustrated with these schemes, a ventilation certification to sign of a bathroom extract fan, not a full blown laundry. or such with dampers and actuators linked to the F/Aalarm system... just a 100mm bathroom fan . We are doomed I tell you.... doomed
Better for the client though as ive seen some bad installs.
 