I believe the correct term as used in BS7671 (17th edition) is Supplementary Equipotential Bonding. This is a method for providing additional protection.
That aside, there is no regulation in BS7671 or ESQCR that prohibits the exportation of a PME earth.
Individual DNOs can and do put restraints on where and to what they will allow connection to their PME system, but that is their choice, not something contained in any standard or statutory document.
There are prohibitions on providing a connection to a PME system for caravans, petrol stations and marinas, obviously exporting a PME earth in such situations would also be prohibited.
The thread from the IET forum you quoted concerned a mobile shipping container, these are often treated the same as caravans. The OP in that thread erroneously believed that a PME earth cannot be exported, hopefully he went away eductaed to the fact that it can be.
One of the problems with exporting a PME earth to an outbuilding containing extraneous parts, is that those parts may well be at a differnt potential to earth than the exported earth. The use of protective bonding will equalise any potential difference, but an appropriately sized protective bonding conductor back to the point of supply will have to be installed.
Often it is more cost effective not to export the earth, and to TT the out building.
danny
Because my interpretation of the regs is different from other peoples doesn't mean that im causing problems at all, on the contrary, it is others if you read the earlier posts who are derogatory to me, please read the posts back, this is a forum not a text book, and different people have different opinions danny
im not saying its a text book, all im saying is iv been on here and needed advice regarding all sorts and someone has help me, the people that have helped me you seem to be having a problem with. imo everyone has there own opinion which is fine but please respect the member on here!!!
danny
danny
Why do you think people have a problem with me?
The problem was never about your opinion, as you say you are entitled to it. It was the fact that at the start of this thread you told the op that they can not export a tncs earth. You did not state this as your opinion, you stated it as fact. Which it is not.
An opinion is a fact of the person sending the message as a fact, which is his opinion is correct.
Reply to Exporting the earth? in the Electricians' Talk area at ElectriciansForums.net
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...