M
Mr Mark Sparks
what is the procedure for having a tt installation changed to tncs ?
who do you call billing company or dno?
also what will they want to see ?
Contact the billing company they will tell you what they need and if they are prepared to do it will either do it themselves or subcontract to the local dno
Chris
Hi Mark,
You need to contact the DNO for this.
Basically just ask for a PME enquiry and they will book a date to come and have a look and convert if they can.
One easy way to tell before the get there, is have a look at the overhead lines.
If its a single cable entering the property then generally it can be converted.
Also, have a look along the road at every 3rd pole. if there is a cable coming down to the bottom then again, it should be ok for PME.
The DNO's have a target to be rid of all TT systems by 20 something, so most of the time its free.
You could always ask when you phone them.
By 2013 i heard.Went to a job the other the day and it was supposed to be TNCS.Reading too high.Originally TT,so had to spike it