Discuss tt to tncs in the Australia area at ElectriciansForums.net

Contact the billing company they will tell you what they need and if they are prepared to do it will either do it themselves or subcontract to the local dno

Chris
 
Hi Mark,

You need to contact the DNO for this.

Basically just ask for a PME enquiry and they will book a date to come and have a look and convert if they can.

One easy way to tell before the get there, is have a look at the overhead lines.

If its a single cable entering the property then generally it can be converted.

Also, have a look along the road at every 3rd pole. if there is a cable coming down to the bottom then again, it should be ok for PME.
 
The DNO's have a target to be rid of all TT systems by 20 something, so most of the time its free.

You could always ask when you phone them.
By 2013 i heard.Went to a job the other the day and it was supposed to be TNCS.Reading too high.Originally TT,so had to spike it
 

Reply to tt to tncs in the Australia area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
828
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Fitted a remote second consumer unit to a detached annex. The supply to it was from a tncs system. The new db has been changed to a tt system for...
Replies
1
Views
758
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock