Hi Guys, I`ve got 2 x 3core 6mm SWA cables to run overhead from a Barn to the chimmney of house and the run is 20m.

Never done this before, do you think this can work and how? I`m concerned about the weight
 
a good catenary should hold it, but it may pull the chimney down in a fair wind.
 
no chance of running underground?
 
no chance of running underground?

absolutley not, customer been sold a big solar system and told by surveyor "overhead not a problem". Muggins here got to sort it out, customer is already fed up after coughin up lots of dosh
 
You’re starting this tomorrow?

It’s a wind up it’s got to be. Mind you looking at some of your posts……
 
I think raw bolts for the hook plate on the chimmney at least or anyone got any better suggestions
 
When you say surveyor this suggests a survey (which I'm assuming would include a risk assessment) has already been done. What was in the survey results?

"SURVEYOR" wrong choice of words, salesman or whatever you want to call it. Lets just say he`s not clued up when it comes to the electrical side of things
 
I think raw bolts for the hook plate on the chimmney at least or anyone got any better suggestions

I wouldn't just fix into the stack, I'd try and get something around the base, along the lines of a TV aerial fixing, and attach the cantenary to that.
 
With 2 x 20meter lengths of 6mm x 3 core SWA I would get a structural engineer in to sign off a satisfactory spec. There's a very good chance a chimney won't support the load.
 
Have you ever tried lifting half a coil of 6mm SWA!!! Good luck trying to fix that! As someone has said, i'b be looking at getting something around the base of the stack as least.

Rich
 
With 2 x 20meter lengths of 6mm x 3 core SWA I would get a structural engineer in to sign off a satisfactory spec. There's a very good chance a chimney won't support the load.

I agree, not going ahead with it, its very exposed and a strong wind will put to much load on the chimmney.

Thanks guys
 
I agree, not going ahead with it, its very exposed and a strong wind will put to much load on the chimmney.

Thanks guys

You wouldn't need SWA overhead, use something lighter and make permanent joints to SWA at the ends on the buildings.
 