There are two options, either remove the earth rod, or as you say, run a 10mm² earthing/bonding conductor from the house.
To my mind the best answer is to remove the rod.
Thanks Spinlondon, The present earth is only a 1.5mm back to the cu in the house, so i think i shall install a 10mm earth back to the , i could leave the earth spike though. Does that make sense?
Cheers
Flyer
I don't know if it makes sense?
What's the difference in cost for installing the 10mm² as oposed to disconnecting the rod?
What is the run back to the CU in the house like? Can you protect (in fact do you need to) the 10mm2 cable. How far is it.
hi Spartykus
The total run is about 18metres from CU to Cu. Trying to run it so it is hidden as mush as possible, don't believe it wil need extra protection. Will need however to drill through external wall as close to the CU as possible.
Flyer
Spin how did you do a proper "squared" symbol...?
At the bottom of the text box is tab "Go Advanced" click that and then toggle "x[SUP]2[/SUP]" from the right of bottom row tool bar.
SO, why not just lose the 1.5 and keep the rod? If the rod is good, if the Ze is good...
Garage is a TT. Save 10mm back to the MET. £40.
Shoulda made good the armour, armour is your friend.
Keep the rod and do away with the 1.5. Disconnect the armour at the garage end so your not exporting the TNCS.
PS. Can anyone enlighten me why 10mm is the minimum?
I thought was 4mm? Or is that if its mechanically protected and against corrosion?
Sent from my GT-I9100 using Tapatalk
10mm² is the minimum CSA for both main earthing and bonding conductors, where PME conditions apply.
Reading a publication from the IEE a few years ago (wriiten by John Ware), it states that you only need to supply a 10mm to an outbuilding if there are extraneous-conductive-parts entering said outbuilding. Therefore, if there is no water pipe etc. entering the garage you wouldn't need a stake or a 10mm earth back to the CU, merely the cpc of the supply cable and an RCD in the circuit.
Please throw some regs at me if this is no longer the case.
That's correct, ....no extraneous-conductive-parts, then no need to bond anything, and no need for a bonding conductor!!!
flyer,
Engineer54,