Hi Guys,
I am working in a house where the client wants a smoke detector changed to a carbon monoxide detector. The detector is currently interconnected with 3 others. Is it just a case of a straight swap with a manufacturers compatible detector would i be better just wiring an independant detector of a mains local lighting feed?

cheers guys:smartass2:
 
Wire it independently, smoke alarms and carbon monoxide alarms should not be interconnected on the same circuit, because they activate for different reasons. This could lead to someone hushing a smoke alarm system due to a suspected false alarm, when in fact there is a high amount of carbon monoxide present.
 
thats a good point sirkit breaker. its easy to wire of the local lighting circuit too. thanks
 
Why don't you use the same cable but strip connect the link wire(s) inside the CO detector. I am assuming there is a three core and earth feeding the smokes. Would save a little work.
 
Is it not possible to keep the existing smoke detector and just add a Carbon Monoxide detector to the room as well?
 
i would never replace a smoke detector with a CO detector, even if it were a viable option. the reason is that the customer would then have lost part of his fire protection system.
 
the detector is a heat and the kitchen is being moved to a new extension. the boiler will now be in the old kitchen so client wants co fitted
 
Yep!

Aico do a switch that when alarm is sounding it will identify which device is setting the alarm off. Without something like that I'd not interlink the Carbon Monoxide alarm with the Smokies. That way if its just the Carbon Monoxide alarm going off the occupier will know that's the problem.
 
The new kitchen should then have a heat detector added if its a new extension which should be linked to the other smokes in the house. I havent seen a CO detector that's link able to other smoke detectors. Are all the bedrooms and living room serviced by the other smoke detectors.
 