Next Question.... how long should i perform CPR on my work collegue before i give it up a no hoper!...
When you say ''Transformer Feeder'' what are you referring to the MV side or the LV side of things?? I'm assuming your talking about the LV side, but best to confirm.... lol!!
Come on tomnoel, What problems are you having with this feeder breaker, for you to want to negate the earth fault protection from this breaker???
During recent testing our TX feeders tripped on inrush To over come this it has been suggested that we turn off the Instantaneous Earth Fault Setting on the TX feeders and still achieve grading with the UKPN relay at the max earth fault setting of 1.5KA. Any Comments.
I can’t see how inrush is showing as earth fault, instantaneous overload maybe. As E54 has asked is this the MV or LV side that the fault is being detected. An incorrectly set restricted earth fault on the LV side is a possibility, but it’s a remote one.
Who has recommended disabling the earth fault, it’s not something you would do as a permanent fix. Can the time lag be adjusted?
One last question, is this a new fault or a long running sarga.