sima24
hi guys, changed a cu on monday, in quote i gave full price, amd listed hourly rate for any faults found. changed board/tails/bonding all good until testing. no continuity on either ring, zs readings at sockets way too high, ze was fine though. after further investigation i have found that most the sockets are spurs, my guess is they have broken the ring somewhere with all these spurs and are basicly left with 2 radials. Rcds stay in tho. problem is he doesnt want to spend anymore money? but im not happy leaving it as it is, what to do?