sima24

hi guys, changed a cu on monday, in quote i gave full price, amd listed hourly rate for any faults found. changed board/tails/bonding all good until testing. no continuity on either ring, zs readings at sockets way too high, ze was fine though. after further investigation i have found that most the sockets are spurs, my guess is they have broken the ring somewhere with all these spurs and are basicly left with 2 radials. Rcds stay in tho. problem is he doesnt want to spend anymore money? but im not happy leaving it as it is, what to do?
 
Test the circuits before you change cu, I test the ring continuity as I'm removing the old cu.
got caught out just the same once, never again
 
hi guys, changed a cu on monday, in quote i gave full price, amd listed hourly rate for any faults found. changed board/tails/bonding all good until testing. no continuity on either ring, zs readings at sockets way too high, ze was fine though. after further investigation i have found that most the sockets are spurs, my guess is they have broken the ring somewhere with all these spurs and are basicly left with 2 radials. Rcds stay in tho. problem is he doesnt want to spend anymore money? but im not happy leaving it as it is, what to do?

if he doesn't want to spend money to fix it theres not alot you can do, invoice him for the board change and put it on the invoice in writing "this installation is unsafe and needs remedial works"
simple as that.
 
how do you know the rings broken anyway?....it maybe that you have tested end to end...each end belonging to a different ring.....
safe iso on all circuits then retest (end to end resistances) between all `ring finals`...check to be sure before anything else...
 
as if you do have a scenario with 2 crossed rings....you wont acheave safe isolation by 1 MCB alone...
 
cheers, I have already weitten on invoice but am trying to convince him to have it checked, even if i have to do it for next to nothing id be happy. lesson learnt i suposse, might use some work contract forms stating that customer is happy for remidial works and get it signed before starting.
max zs on the sockets (tncs) 1.16, i was getting 1.7+. i dont usualy test zs i calculate but didnt have a r1 r2 to work with
 
I bill for a test first, then knock it off the board change price....always good to find the faults before removing the board.....borrowed neutral on stair lights caught me out once!!!
 
Iv already tested to make sure i have correct ends, buzzed out to first socket on each "ring", picking up on 1 leg but no return leg. Never had a problem with customers before, if i find a fault i explain it in simple terms to the customer and say exactly how i will repair/find the problem, and im upfront about my fees. I think this guy is looking at the board and thinking "well its safer than it was before"
 
max zs on the sockets (tncs) 1.16, i was getting 1.7+. i dont usualy test zs i calculate but didnt have a r1 r2 to work with

I think you may have missed S1973's point in post #3 :thinking2:, also as the poster said in post #4 put the radials on a 20A MCB after checking confirming as per posts #6&7, it is valid to have your junction at the MCB :icon12:

Also regardless of additional protection, your max Zs is higher for a 20A B type MCB.
 
Because i would rather connect it back on a ring. If installing as 2 radials is it not going to cause any problems with labelling, and cant see how zs readings would improve
 
The 1.7ohm readings are probably just corroded terminals on your plug in lead, If you are doing the eli test on D-lok, the readings are generally higher then the true readings anyway.
 