would a high ZS also cause problens with overcurrent protection

You so know why we measure Zs dont you?

Yes it could cause the OCPD to not trip in the desired time.

Do they not teach anything at college these days?
 
if the Zs was , say, around 20% higher than the BS max, figure, i would be inclined to look more closely at the current demand of the circuit and, if possible, reduce the rating of the OCPD.
 
my college was good, but i turned up and listened cause had to pay for it myself.. and for some reason got more interested and interested on how this all comes together.... still long way to go where expierience comes in
 
If you are unable to obtain a satisfactory Zs reading on bathroom circuits, you would also have to provide supplementary bonding along with RCD protection.
 
I had a situation recently at a very big house where an old ring final had been installed using T&E with a 1mm CPC, and circuit length was over 250m. Zs were unsatisfactory. Unfortunately they had recently decorated the place, so rewiring was out of the question. I looked at loading on the circuit and it was only serving two bedrooms at the far end of the house, so I reduced the breaker from 32a to 20a, and also added RCD protection. I had thought about adding a submain to serve the far end of the property but they wouldn't go for it.
 
You are missing the point though....Zs is only measured after R1+R2 has been measured on a new circuit....if it's a TN system,and continuity and Ze readings are within expected limits,then Zs will be satisfactory. If it's not something is amiss which has nothing to do with earth loop impedance and should have been rectified long before the ELI tester comes out.
Another point often forgotten by the 'you cant use an RCD for earth fault protection,it's additional protection only' brigade is that nearly all TT systems in the UK rely solely on one or more RCD's for earth fault protection.

Well i am definitely 100% in the additional protection brigade for TN installations then!! lol!!

We all know only too well that a TT system is a whole new ball game, Especially the newer UK TT systems. ...That's if you can even call some of them a TT system!!

Somethings certainly is amiss, if your ADS system doesn't meet disconnection times, ...end of story!! And using an RCD to get you out of jail, isn't going to rectify the deficiency either. Far too much of this RCD cure all philosophy seems to be going on in the UK these day's.
 
thats what they getting taught, even says it in bs 7671 what we work too, so what do you expect china man..?
 
thats what they getting taught, even says it in bs 7671 what we work too, so what do you expect china man..?

Frankly, ...Nothing!! Just happy that i don't have to work in an environment that has lost it's way and where it seems standards are falling away like nine pin's!!
 
No can't just put an RCD on it, what is the circuit, design, length, number of points.
For example if it is a ground floor ring main work out what the load will be, you may be able to convert it into a radial or two radials to help spread the load, so by then using a 16a instead of 32a mcb you have nearly doubled your max zs, or if a different circuit work the load out if you can use a lower mcb this will give you a higher max zs
 
Well i am definitely 100% in the additional protection brigade for TN installations then!! lol!!

We all know only too well that a TT system is a whole new ball game, Especially the newer UK TT systems. ...That's if you can even call some of them a TT system!!

Somethings certainly is amiss, if your ADS system doesn't meet disconnection times, ...end of story!! And using an RCD to get you out of jail, isn't going to rectify the deficiency either. Far too much of this RCD cure all philosophy seems to be going on in the UK these day's.

I know where you stand on this.......but some time back I had an existing circuit in a school which served benches of computers....a master switch isolated all the sockets so that the teacher on leaving could switch off all computers in one hit at the end of the day. Trouble was on switch on in the morning the type C MCB would occasionally trip due to the starting surge....on checking it was found Zs was just too high for a type D....but the fact that a 30ma RCD was on the circuit meant that the max Zs for a type D OCPD could be ignored....since it was fitted there have been no further problems.
That is the scenario I am referring too when I say an RCD can be used for a high Zs.....nobody in their right mind would accept a Zs way outside the expected reading just because there is an RCD in circuit.
 
nobody in their right mind would accept a Zs way outside the expected reading just because there is an RCD in circuit.


I think you would be surprised just how many would do exactly that, on finding a Zs way outside the value expected. It's just too easy not too!! lol!!​

​
 



I think you would be surprised just how many would do exactly that, on finding a Zs way outside the value expected. It's just too easy not too!! lol!!​

​

Maybe.....but then they'd have to jackanory their R1+R2 ,Ze and Zs results in order to make it look right on the cert.......you dont really think that sort of thing goes on do you?
 