pete555
would a high ZS also cause problens with overcurrent protection
would a high ZS also cause problens with overcurrent protection
You are missing the point though....Zs is only measured after R1+R2 has been measured on a new circuit....if it's a TN system,and continuity and Ze readings are within expected limits,then Zs will be satisfactory. If it's not something is amiss which has nothing to do with earth loop impedance and should have been rectified long before the ELI tester comes out.
Another point often forgotten by the 'you cant use an RCD for earth fault protection,it's additional protection only' brigade is that nearly all TT systems in the UK rely solely on one or more RCD's for earth fault protection.
thats what they getting taught, even says it in bs 7671 what we work too, so what do you expect china man..?
would a high ZS also cause problens with overcurrent protection
yes it wouldnt operate device in designed time to save life
Well i am definitely 100% in the additional protection brigade for TN installations then!! lol!!
We all know only too well that a TT system is a whole new ball game, Especially the newer UK TT systems. ...That's if you can even call some of them a TT system!!
Somethings certainly is amiss, if your ADS system doesn't meet disconnection times, ...end of story!! And using an RCD to get you out of jail, isn't going to rectify the deficiency either. Far too much of this RCD cure all philosophy seems to be going on in the UK these day's.
nobody in their right mind would accept a Zs way outside the expected reading just because there is an RCD in circuit.
I think you would be surprised just how many would do exactly that, on finding a Zs way outside the value expected. It's just too easy not too!! lol!!