Hi team,
Control panel for 2 submersible pumps, duty, assist.

Need to come up with something to confirm pumps running, not just signal to do so.
Was thinking ct on the outgoing connections but I would need a pair of voltage free contacts from this to create a confirmation signal.
Is there a Siemens or similar module known to do this?

Thanks,

Boydy
 
Use a N/O auxiliary contact on your main contactors to feed a couple of indication lights?
Simple but effective.
 
This wont confirm the pumps are running only that the contactor, or power out is present, you need a fail safe indicator with possible alarm and using a flow sensor is the best bet here as any issue with motor, supply, water etc will come up as an alarm, it dosn't rely on the fact if the motor is powered then its working which isn;t always the case.
 
Thanks Al but that only confirms the command and contactor closure.
I need to know pumps are running, drawing current.
For example if a downstream isolator was off, no current drawn.

Boydy
 
We are limited to set up knowledge here but so many options exist, current monitoring relays, ameters with CT clamps you can purely use them for indication or intergrate them for fuctional control if conditions are not met, would have to know exactly what the customer needs and the consequences of pump failure to know best route... some times you need to tell customer the best way not just agree to his request, if motor impellor broke the current would still show albiet lower value but oil/water flow would be lost and no-one the wiser until possible machine damage etc occurs ....

It might seem overboard but a risk assessment is needed when adapting controls as to why your fitting them, what happens in various circumstances and would damage occur or down time be costly.
 
Thanks DW,

What is needed is a remote signal to confirm non run after command received.
Pump impeller or thermister etc faults would go out on alarm anyway and then the non run (higher priority) signal would go out next time a command was given and not responded to.

Thanks,

Boydy
 
Thanks Al but that only confirms the command and contactor closure.
I need to know pumps are running, drawing current.
For example if a downstream isolator was off, no current drawn.

Boydy

Very true and agree with you and Darkwood.

Its a method we employ on Haz. area panels for a hydraulic pump unit...............indication lights for the operator e.g motor run/motor/stopped/tripped/lamp test etc.
Panels are normally mounted next to the motor so the noise lets him know it's actually running lol.

Totally different if the motor is remote from the panel though like you both have stated.
 
Boydy,
What about using a flow meter with a 4-20ma output (or similar) that you can connect to an analog input on your control circuit, then you will have an indication if you have a blockage etc ?

Regards,

Dave
 
Another option might be for a pressure sensor on the output side of the pump, or two sensors, one either side of the pump?
 
Easiest option would be a three phase current monitor, no plumbing involved, no cables to run. RS is selling them, but not cheap.
 
Simple always works.

Use a pressure switch in series with a N/O contact on the contactor.

It will confirm the pump is actually pumping something.
 
The only problem I can see with a flow mwter, is that the business end may restrict the flow.
 